NetApp Stage KB
Call home for BATTERY (voltage critical low) CRITICAL
Visibility:
Votes:
0
Category:
ontap-9
Specialty:
HW
Last Updated:
Applies to
FAS2820
Issue
  • Shutdown occurred on node due to battery.low:ALERT: Call home for BATTERY_LOW.
system log:
Jul 03 17:35:27 [localhost:nvmem.battery.voltageLow:EMERGENCY]: The NVMEM battery voltage is critically low (5400 mV). To prevent data loss, the system will shut down in 5 minutes.
Jul 03 17:35:28 [localhost:nvmem.battery.capLowCrit:EMERGENCY]: The NVMEM battery capacity is critically low (0 cycles). To prevent data loss, the system will shut down in 20 minutes.
Jul 03 17:35:29 Power outage protection flash de-staging: 0 cycles
WARNING:  The battery is experiencing a critical failure:
- Battery voltage is in critical state
Without a working battery, the system cannot retain data
during a power outage, which can result in data loss.
Power down the system and verify that the battery is
properly installed.
To ignore this failure and boot the system in a mode
where data loss might occur, press 'c' followed by 'Enter'
Jul 03 17:35:57 [localhost:callhome.battery.failure:EMERGENCY]: Call home for BATTERY (voltage critical low) CRITICAL.
Jul 03 17:35:57 [localhost:callhome.battery.failure:EMERGENCY]: Call home for BATTERY (remaining destage cycle is zero) CRITICAL.
WARNING:  The battery is unfit to retain data during a power
outage.  This is likely because the battery is
discharged but could be due to other temporary
conditions.
When the battery is ready, the boot process will
complete and services will be engaged.
To override this delay, press 'c' followed by 'Enter'
Jul 03 17:37:31 Power outage protection flash de-staging: 0 cycles
c
CAUTION: Using this appliance without NVRAM
battery backup coupled with a power
failure condition CAN CAUSE DATA LOSS.
Are you sure you want to continue (y or n)? y
Proceeding without NVRAM battery backup.
Pensando Offload Driver, ver 1.4.0-E-78
***OS2SP configured successfully***RC NIC fw update error is :0
NIC FW update from kernel error is :0
Jul 03 17:39:05 [localhost:extCache.enabled:notice]: WAFL external cache administratively enabled
Jul 03 17:39:05 [localhost:extCache.rw.terminated:notice]: WAFL external cache warming process terminated.
Jul 03 17:39:05 [localhost:extCache.rw.replay.canceled:notice]: WAFL external cache replay canceled for aggregate aggr0: Aggregate came online after timeout.
Jul 03 17:39:05 [localhost:cf.fsm.takeoverOfPartnerDisabled:error]: Failover monitor: takeover of partner disabled (Controller Failover takeover disabled).
Jul 03 17:39:05 [localhost:monitor.nvramLowBattery:EMERGENCY]: NVRAM battery is dangerously low.
Jul 03 17:39:05 [localhost:monitor.nvramLowBattery.notice:notice]: If the NVRAM battery is dangerously low, the system shuts down automatically every 24 hours to encourage you to replace it. If you reboot the system it will run for another 24 hours before shutting down.
Jul 03 17:39:05 [localhost:callhome.battery.low:ALERT]: Call home for BATTERY_LOW.
  • FRU LED ID 1 (System Attention LED), 3 (Controller Attention LED), 6 (SAS Port A Attention LED), and 15 (NV BATTERY Attention LED) are On.
get_leds
FRU LEDs status
FRU LED ID 1  = Controller Locate LED
FRU LED ID 2  = System Attention LED
FRU LED ID 3  = Controller Attention LED
FRU LED ID 4  = Controller Active LED
FRU LED ID 5  = NV Destage Status LED
FRU LED ID 6  = SAS Port A Attention LED
FRU LED ID 7  = SAS Port B1 Attention LED
FRU LED ID 8  = SAS Port B2 Attention LED
FRU LED ID 9  = 25G Port 1 Attention LED
FRU LED ID 10 = 25G Port 2 Attention LED
FRU LED ID 11 = DIMM Slot 1 Attention LED
FRU LED ID 12 = DIMM Slot 2 Attention LED
FRU LED ID 13 = NVME 1 Attention LED
FRU LED ID 14 = M2 SATA Attention LED
FRU LED ID 15 = NV BATTERY Attention LED
FRU LED ID 16 = Coin Cell Attention LED
FRU LED ID 1 is off
FRU LED ID 2 is on. Set by BMC
FRU LED ID 3 is on
FRU LED ID 4 is off
FRU LED ID 5 is off
FRU LED ID 6 is on
FRU LED ID 7 is off
FRU LED ID 8 is off
FRU LED ID 9 is off
FRU LED ID 10 is off
FRU LED ID 11 is off
FRU LED ID 12 is off
FRU LED ID 13 is off
FRU LED ID 14 is off
FRU LED ID 15 is on
  • Since the critical error continues in system sensors after startup, this is likely an NVMEM battery failure.
Sensor Name              State          Current    Critical     Warning     Warning    Critical
Reading       Low         Low         High       High
Bat FRU LED                                 ON
Battery RemCap Desc                      READY
Battery Charge Failed?                    TRUE
Battery Charge Bad?                       TRUE
Battery Capacity Message failed             --
Voltage Spike Frequency  crithigh           6          --          --          --           3
Voltage Status                             BAD
Temp Low Shutdown                           UP
Temp High Shutdown                          UP
SNMP Bad Fan Count                          OK
Chassis Temperature unreadable                  YES
CPU Temp Margin          failed            -- C        --          --         -11 C        -1 C
CPU Core Temp            failed            -- C         0 C         5 C        90 C       100 C
PCM Inlet Temp           normal            29 C         0 C         5 C        67 C        72 C
M.2 Card Temp            normal            32 C         0 C         5 C        95 C       100 C
DIMM Temp                normal            30 C         0 C         5 C        80 C        85 C
SAS Temp                 normal            29 C         0 C         5 C       100 C       105 C
P12V                     critlow          124 mV    10540 mV    10850 mV    12958 mV    13454 mV
P12V Standby             normal         12028 mV    10540 mV    10850 mV    12958 mV    13454 mV
P12V Curr                critlow            0 mA        0 mA       --          --       15810 mA
P5V                      critlow            0 mV     4264 mV     4368 mV     5694 mV     5824 mV
P5V STBY                 normal          5018 mV     4264 mV     4368 mV     5694 mV     5824 mV
PVCCIN CPU               critlow            0 mV     1249 mV     1470 mV     1932 mV     2026 mV
PVDDQ DDR4 AB            critlow            0 mV     1050 mV     1100 mV     1299 mV     1349 mV
PVTT DDR4 AB             critlow            0 mV      518 mV      546 mV      653 mV      681 mV
P3.3V                    critlow            0 mV     2887 mV     3027 mV     3570 mV     3710 mV
P3.3V Standby            normal          3307 mV     2887 mV     3027 mV     3570 mV     3710 mV
P2.5V Standby            normal          2508 mV     2191 mV     2296 mV     2706 mV     2904 mV
P1.2V Standby            normal          1214 mV     1050 mV     1100 mV     1299 mV     1398 mV
P1.15V Standby           normal          1164 mV     1022 mV     1050 mV     1249 mV     1341 mV
Coin Batt 3V             normal          3017 mV     2538 mV     2707 mV     3299 mV     3440 mV
Bat Present                             PRESENT
Bat Temp                 normal            28 C         0 C         5 C        60 C        75 C
Bat Volt                 normal          6100 mV     5500 mV     5600 mV     8500 mV     8600 mV
Bat Curr                 normal             0 mA       --          --        1200 mA     1520 mA
Bat Rem Cap              normal             0 W*hr     --          --          --          --
Bat Dstg Cycles          critlow            0 cycles    2 cycles    5 cycles   --          --
Bat Full Cap             normal            16 W*hr     --          --          --          --
Bat Initial FCC          normal            20 W*hr     --          --          --          --
Bat Charge Curr          normal          1000 mA       --          --        2200 mA     2300 mA
Bat Charge Volt          normal          8200 mV       --          --        8900 mV     9000 mV
Bat Dcharge FET                             ON
Bat Charge FET                              ON
Bat Cycle Count          normal             0 cycles   --          --          --          --
Bat Learning Active                        OFF
Bat Pack Invalid                            OK
Bat Charging State                      NO_CHARGE
Bat Pct Capacity         normal            80 %        39 %        44 %        --          --
CPU Error                               NORMAL
CPU Therm Trip                           FAULT
CPU Hot                                 NORMAL
Memory Hot                              NORMAL
Wrench Port Up                              UP
HIC 0 Temp               not_available     -- C         0 C         5 C       100 C       105 C
HIC 1 Temp               not_available     -- C         0 C         5 C       100 C       105 C
HIC Sensor                              TWO_HIC_SENSOR
BMC Reboot policy                           ON
Attention                               ASSERT
Reboot BMC                                  NO
NV0 Battery State                       PARTIALLY_DISCHARGED
NV0 Battery Voltage      normal          6100 mV     5500 mV     5600 mV     8500 mV     8600 mV
NV0 Type                                TYPE_NVMEM
Mgmt Port Count          normal             1          --          --          --          --
Bat Count                normal             1          --          --          --          --
Thermal Zone Count       normal             1          --          --          --          --
Fan Count                normal             4          --          --          --          --
PSU Count                normal             2          --          --          --          --
Mgmt Port Link           normal             1          --          --          --          --
Battery Charge           failed             --
Dblade Battery Status                   PARTIALLY_DISCHARGED
Dblade Temp                             NORMAL_TEMP
init                     invalid            -